Thought I would post this for general comments. Yesterday I inspected a 4000A, 480/277V, 3ph, 4 wire switchboard installation. The day-before, the cables (13 sets 500kcmil) had been pulled out to a utility company, pad-mount xfrmer and also terminated at the landing lugs of the board.
Problem is, the contractor pulled what looks to be 20 to 25feet of extra cable and just had it all coiled up in the bottom of the switchboard section. 13 sets x all the footage....Its a mess.
Anyone ever see anybody do that? In over 25 years of consulting practice, I've never seen that. Besides some additional voltage drop, it looks like a big AC choke, inductance, not to mention a rat's nest.
I'm writing the report now and directing them to not energize the transformer until this is undone, cut to a reasonable length, assure same distance on all parallels, and then reconnect.