liam1369
Structural
- Nov 13, 2014
- 73
Hi All,
As part of a design for a roof perimeter beam, we have a 1.70m high parapet. The beam is 9.0m long and has a steel parapet post in the middle to prop the PFC windbeam at the top of the parapet spanning between main oversailing columns.
Conservatively, we have a moment base at the base of the parapet post, therefore, via calculation it is transferring a torsional moment of 12kNm into the mid span of the beam.
When running a TEDDS calc for moment, shear and torsion at mid-span position it is utilised to 140%!
However, it is not considering the secondary beams which frame in at 2.5m centres, one being very close to the post that comes in. The 130mm deep composite deck that is fixed to along its length and also we have 12 bolt end plates at the ends of the 533x210x109 UB.
I have attached a sketch to confirm section arrangement.
Does anyone have any advice or can pinpoint to some literature or guidance on practical justifications or considerations for perimeter beams like this, otherwise the beam size needs to increase which I think is quite a significant overkill.
Let me know your thoughts.
As part of a design for a roof perimeter beam, we have a 1.70m high parapet. The beam is 9.0m long and has a steel parapet post in the middle to prop the PFC windbeam at the top of the parapet spanning between main oversailing columns.
Conservatively, we have a moment base at the base of the parapet post, therefore, via calculation it is transferring a torsional moment of 12kNm into the mid span of the beam.
When running a TEDDS calc for moment, shear and torsion at mid-span position it is utilised to 140%!
However, it is not considering the secondary beams which frame in at 2.5m centres, one being very close to the post that comes in. The 130mm deep composite deck that is fixed to along its length and also we have 12 bolt end plates at the ends of the 533x210x109 UB.
I have attached a sketch to confirm section arrangement.
Does anyone have any advice or can pinpoint to some literature or guidance on practical justifications or considerations for perimeter beams like this, otherwise the beam size needs to increase which I think is quite a significant overkill.
Let me know your thoughts.