AKM30 said:
I am not sure where the torsion on the joists is coming from in my structural model.
1) It's pretty hard for a CIP system, one way or other wise, to not behave a bit like a two way slab in the real world and in a 3D model. And two-way slabs have twist/torsion. So your ribs are going to pick up some twist/torsion. It makes sense to me that you would see some of that.
2) For these kinds of systems, there's always an interplay between flexural stiffness and torsional stiffness. I believe that the stiffer you make your system flexurally, the less torsion your ribs will pick up. Which is not to say that there's anything wrong with your current design. I agree with JAE's take on this although I haven't yet come up with a good argument for why the torsion should be ignored other than a) we always do that and b) nothing ever seems to come of it.
3) Well, maybe I do have one plausible argument for ignoring the torsion. The torsion in the stems would have to be transmitted to those stems via flexure in the topping slab. I suspect the topping slab would crack and shed stiffness long before you picked up an appreciable torsion in your ribs.
Out of curiosity:
1) What's the joist span?
2) What's the joist width?
3) What's the total depth of the system.
4) What's the width of the floor panel perpendicular to the span?
5) What is the spacing of the ribs?
6) What support conditions have you modelled around the perimeter of the floor panel? CIP girders?