I have a small strip of a precast concrete piece that is very lightly loaded in service and is being reinforced with small mats of WWR. Essentially it's acting as a beam connecting two walls. However, during stripping, transport, and placement there's a genuine concern that someone will put this beam into torsion.
To resist this I'm hoping to use leftover pieces of the WWR bent into a cage inside the beam as specified in ACI 318 11.5.4.1(b). This should be a cheap and easy way for the precaster to reinforce this without spending a lot of extra time bending and placing stirrups.
However, because I'm using a WWR cage I don't see how I can easily provide the 135-degree standard hook required by 11.5.4.2(a). I don't really have anything meeting the alternative requirements of 11.5.4.2(b) to resist spalling around the anchorage.
Does anyone see a way around this? Seems that this grossly limits the use of a WWR cage in place of stirrups to only members with slabs, flanges, or similar to resist spalling as required by 11.5.4.2(b)
Maine Professional and Structural Engineer. www.fepc.us
To resist this I'm hoping to use leftover pieces of the WWR bent into a cage inside the beam as specified in ACI 318 11.5.4.1(b). This should be a cheap and easy way for the precaster to reinforce this without spending a lot of extra time bending and placing stirrups.
However, because I'm using a WWR cage I don't see how I can easily provide the 135-degree standard hook required by 11.5.4.2(a). I don't really have anything meeting the alternative requirements of 11.5.4.2(b) to resist spalling around the anchorage.
Does anyone see a way around this? Seems that this grossly limits the use of a WWR cage in place of stirrups to only members with slabs, flanges, or similar to resist spalling as required by 11.5.4.2(b)