I think I see now. BA, your calculation is for a member fixed at one end, free at the other, with a torque applied at the free end and thus constant over the length. When I apply my method, I get almost exactly the same answer. Using your Mt, dividing by 250, gives a force on each flange of about 5600 N. Applied as a point load at the end, the deflection of each flange is about 10 mm, so the channel leans 20/250, which is about 4.6 degrees.
A one metre long channel, fixed at both ends (like the OP's problem) and subjected to uniform loading along its length, will be subject to varying torsion, and by my method will have only about 0.07 degrees rotation at the middle, using your same Mt at each end.
Perhaps structuralex will give us a real problem, with the span and loading defined, and we can compare results.