Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Tek-Tips community for having the most helpful posts in the forums last week. Way to Go!

Total E.D.R.

Status
Not open for further replies.

opoplectic

Mechanical
Aug 10, 2002
7
0
0
US
I came across a set of mechanical drawings from the 60s and there is reference to "Tot. EDR" in the AHU Schedule under the heating coils. I found out that Tot. EDR means Equivalent Direct Radiation.

Question is how do I convert to MBH.

thanks
 
Replies continue below

Recommended for you

Each square foot of EDR is equivalent to 240 BTU when the coil or radiator is surrounded by 70*F air, and there's steam at 1 PSIG in it.
 
OK - I found the calculation for steam & hot water. It's delta-T (rad to air), in *F, multiplied by 1.6.

With an air temp of 70*F, and an avg hot water temp of 160*F would be:

(160 - 70) X 1.6 = 144 BTU

If you had steam at 5 PSIG:

(227 - 70) X 1.6 = 251.2 BTU
 
Status
Not open for further replies.
Back
Top