AELLC, in addition to the above, I'd like to continue with the following facts:
Please see above layout of the floor. The designers don't do manual computations because they are designing so many buildings so they need sophisticated program like ETABS. They even forgot to manually compute so we are discussing the manual computations and comparing to their ETABS. Please comment on the following. I know the other formula to get tributary area of the slabs in each beam. But since we are computing the concentrated load in the girder/secondary joint, then the shaded area in the picture is the influence of dead & live load. I know there is contribution in the far side of the slab and beam as load varies along the spans but remember the other beams also contribute in supporting the shaded area load but the computation is similar if the entire shaded area is 100% of the load for estimation purpose. Isn't it this approximation is used?
Calculations of dead load
23.54 kN/m^3 (23.54 kN in a cubic meter of concrete)
Beam sections = 500mm depth by 300mm width
Slab thickness - 100mm (4")
Dead Load of secondary beams framing into joint
Beam framing into girder joint 3meters each so 23.54 x 0.5mx0.3m = 3.531x 6 = 21.186 kN
Dead load of the slabs.
23.54 kN/m^3 x 0.1m (thickness of slabs)=2.354 kN/m^2
2.354 x 18 square meters (the shaded area has 18 sq.m) = 42.372
So total dead load of the beam and slab in the girder is 63.558 kN. I didn't include the girder beam self weight because we are getting the concentrated load framing on the joint. Shear Vdl from the deadload is about 63.558/2 = 31.779 kN.
Live Load
assume 4.8 kpa maximum load 4.8 kPa x 18 sq.m - 86.4 kN live load
shear V = 86.4/2 = 43.2 kN
Total load
wu = 1.2 DL + 1.6 LL = 1.2 (63.558) + 1.6 (86.4) =76.2696 + 138.24 = 214.5 KN
or add SD load of tile floor = 23.54 x 0.05m (2") = 1.117 x 18 = 21.186
214.5kN + 21.186 kN = 235.686 Kn
but I plan to remove the entire 2" flooring mortar bed & tiles to reduce load so let's use 214.5kN (I won't allow any partition too in the shaded lines and ceiling weight below is so light because it is just light wooden board so let's ignore it for calculation sake esp since I round off the horizontal span from 5.5m to 6m)
From total wu of 214.5 kN
Vu = 214.5kN/2 = 107.2548 kN (24 kips) concentrated load framing into the girder midspan.
Vc and Vs of the concrete and stirrup is enough to handle 107.2548 kN.
So far, are the calculations above sound at least for 1.2 DL + 1.6 LL?
Of course if you take in seismic, the effect is like twice of 1.2 DL + 1.6 LL and I won't manually compute it. I'd just like to know for now if at least the building shear can support gravity load of 1.2 DL + 1.6 LL
Thanks.