Transfer plate design is a broad and complex topic, particularly if we're talking PT. As such, my response is bound to be woefully incomplete. Regardless, I'll do my best to help.
OP said:
how do you determine the number of tendons, is base on total slab thickness?
The number of tendons required will be based on a number of factors and the total slab thickness will definitely be one of them. The level of prestress is usually specified primarily based on serviceability requirements (deflection). That said, flexural capacity, durability (crack control), and code requirements also factor in among other things.
OP said:
will I need to consider stress at first cast?
You most likely won't be stressing any of your cables until the entire slab has been poured (let me know if that's incorrect). The two stage pour shouldn't have much impact on ultimate flexural strength. It may have an effect on deflection performance however. When the second stage is poured, it will be restrained from shrinking freely by the presence of the first stage pour (already hardened). That will result in some cracking of the concrete that is part of the second stage pour.
With the two pour scheme, you'll definitely need to consider the issue of horizontal shear transfer within the slab. You'll need to assess demand and provide a competent mechanism for shear transfer across the joint such at shear friction etc.
OP said:
do you have anytext book or manual talk about transfer plate steps?
I know of nothing that deals with transfer plates specifically. Some options for general post-tensioned floor slab design include:
Gilbert
Collins
Khan
Aalami
I've found that, for most transfer plates, I prefer not to use post-tensioning. There are two reasons for this:
1) Generally (hopefully) column offsets above and below the slab are modest. As such, thickness is selected based on shear demand and slab deflection is not critical.
2) Often transfer plate loading and geometery is so irregular that it's difficult to arrive at a sensible tendon layout. Sometimes discrete post-tensioned girders end up making more sense than a full post-tensioned floor plate.
I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.