Fast, open transition transfer switch causes upstream circuit breaker trip on transfer. From transformer secondary currents with lower loads that survive without a breaker trip, I see an open time of about 30ms. Feeding a 45kVA dry, three-phase transformer 480V to 160V AC, 55FLA, for generator excitation power. Breakers trip going either direction (normal to emergency, emergency to normal). Upstream breakers are 70A Molded Case Circuit Breakers (MCCB) without adjustable magnetic trip (probably around 3X handle rating). Trips do not occur if we lower the excitation load on the secondary of the transformer. Excitation load is a six-SCR bridge to feed DC to a generator field coil.
I wonder if transformer inrush is exacerbated by having residual magnetic flux reverse the voltage on the primary terminals such as with DC relay coils, generator DC field coils, etc.
In my opinion, the breaker is simply undersized and should be 100A with adjustable magnetic trip set to 10-15X handle rating.
In a previous thread (Breaker tripping with ATS Transfer, thread238-103803), member rbulsara commented and referred to a paper about similar phenomenon, but I cannot find that--references to that paper would be appreciated.
I see lots of references an discussion related to transformer energization inrush but little about inrush after a short open time. Your help and comments are appreciated!
Regards
David
David
I wonder if transformer inrush is exacerbated by having residual magnetic flux reverse the voltage on the primary terminals such as with DC relay coils, generator DC field coils, etc.
In my opinion, the breaker is simply undersized and should be 100A with adjustable magnetic trip set to 10-15X handle rating.
In a previous thread (Breaker tripping with ATS Transfer, thread238-103803), member rbulsara commented and referred to a paper about similar phenomenon, but I cannot find that--references to that paper would be appreciated.
I see lots of references an discussion related to transformer energization inrush but little about inrush after a short open time. Your help and comments are appreciated!