ThePunisher
Electrical
- Nov 7, 2009
- 384
One the existing system we are operating are described as follows:
13.8kV substation (via 34.5kV output circuit breaker) is feeding a remote 13.8kV padmounted switchgear(to the 13.8kV input circuit breaker) via overhead distribution lines. The 13.8kV padmounted switchgear further (via 13.8kV outgoing circuit breaker) feeds a 13.8-4.16KV dry type power transformer and the transformer feeds a 4.16kV switchgear (connected to 4.16kV input circuit breaker.
There are protective relays that protect and trip each of the circuit breakers stated above.
One of our engineering colleagues recommended that there should be a transfer trip from the upstream 13.8kV circuit breaker to the remote 13.8kV padmounted switchgear input circuit breaker and vice-versa.
Our point is that it is not required since if there is a fault at the 13.8kV overhead distribution, the upstream 13.8kV protective relay will trip the associated upstream relay (via 86). Hence, even though the downstream 13.8kV padmounted switchgear input breaker remains closed, the upstream breaker is "locked out".
Will this logic be acceptable in your personal experience? The upstream and downstream equipment are all owned by the plant.
Thank you.
13.8kV substation (via 34.5kV output circuit breaker) is feeding a remote 13.8kV padmounted switchgear(to the 13.8kV input circuit breaker) via overhead distribution lines. The 13.8kV padmounted switchgear further (via 13.8kV outgoing circuit breaker) feeds a 13.8-4.16KV dry type power transformer and the transformer feeds a 4.16kV switchgear (connected to 4.16kV input circuit breaker.
There are protective relays that protect and trip each of the circuit breakers stated above.
One of our engineering colleagues recommended that there should be a transfer trip from the upstream 13.8kV circuit breaker to the remote 13.8kV padmounted switchgear input circuit breaker and vice-versa.
Our point is that it is not required since if there is a fault at the 13.8kV overhead distribution, the upstream 13.8kV protective relay will trip the associated upstream relay (via 86). Hence, even though the downstream 13.8kV padmounted switchgear input breaker remains closed, the upstream breaker is "locked out".
Will this logic be acceptable in your personal experience? The upstream and downstream equipment are all owned by the plant.
Thank you.