Transformer AirCore Reactance

Status
Not open for further replies.

tctctraining

Electrical
Nov 17, 2008
118
For a 15/20MVA, 27.6 to 13.8KV transformer,does anybody know where I can find air core reactance value?

Thanks
 
Replies continue below

Recommended for you

What do you mean by 'air core reactance value'? Transformers of that size are iron cored, liquid filled except in very unusual cases.


----------------------------------
image.php

If we learn from our mistakes I'm getting a great education!
 
I think he means the inductance of the coil disregarding the core. I'm not sure if this is typically looked at for power transformers, but it's a common value to discuss for VTs to see how they will react when saturated. When the core is saturated, the reactance is virtually the same as the air-core reactance.
 
pwrtran-

Asking for the air-core reactance of an iron-core transformer is to indicate the properties WHEN saturated.

 
Air Core Reactance: REAL Constant: Usually approximately twice the leakage reactance [pu]

I am modeling a transformer inrush urrent through PSCAD. One of the ways to simulate high inrush is through changing saturation constants- The other variable is the Knee Voltge.

The software default value is 0.14 p.u.
 
Probably can just use an inductor air core calculation (solenoid), and run the calc on the primary winding, since the secondary would not be linked much without the core effects.
I haven't heard anyone request this before. For inductors it's clear. This would be the point where the core's relative permeability is 1. So it's as though the core isn't there. This is really more a theoretical number since It would take so much current in an inductor that the coil would burn up straight away or come apart from short circuit forces. But in a transformer, to achieve true hard saturation requires extreme overvoltage to the point of likely turn to turn isulation failure. Even if that didn't occur, the exciting current would be extreme, just like in the inductor.
If you just want to know the short circuit impedance, then the transformer's rated impedance will probably be adequate. ie 4%Z => 1/.025 = 40 times rated amps. That's all the current a bolted fault would develop.

Neil
 
Wikipedia has several calculations if you look under Inductor. I would think a transformer primary would be the same.

Neil
 