Transformer charging with Generator

Status
Not open for further replies.

sakaran51

Electrical
Mar 27, 2013
61
Hi,
Can anyone throw some light on the long term impact on the generator,energizing the transformer?
A 5 MVA 33/11kV Transformer needs to be charged with a 10MVA,11kV Steam Turbine Generator.Is there any thumb rule for Generator-Transformer charging?
 
The best solution when possible is to connect the transformer to the generator before starting the generator.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
Dear Waross,
I do agree with your recommendation.But in practice it is not always possible to charge the transformer with the generator directly connected as a single unit.Hence I am wondering is there a cut off limit by which we can design and operate plant electricals,which will be of some guideline.
 
I suggest searching this site for information. There have been some good discussions of methods to mitigate transformer inrush.
You may consider pre-charging,- That is energizing the transformer through current limiting resistors and then shorting out the resistors.
I seem to recall also some discussion of a method to reduce the residual magnetism when a transformer is de-energized to avoid the worst case asymmetrical energization surges.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 