Transformer clearance from Oil containment

082399

Electrical
Dec 10, 2006
3
Good day
Hi,
Would like to hear some advice from oil containment experts, Is there any specific rule of thumb, regulations or standard clearances from Transformer radiator to the inner wall of
Oil containment, I would like to share the outline drawing. Just to ensure that this installation is not violating any code.
My Transformer spec is a 150 MVA Transformer with a capacity approx 22,500 gal of oil.

Thank you.
 

Attachments

  • Transformer and Oil Containment.JPG
    Transformer and Oil Containment.JPG
    91.7 KB · Views: 24
Replies continue below

Recommended for you

We size the transformer bund to contain a 26.5° oil spray from the top of the tank, radiator, bushing turrets, and the bottom outlet from the conservator. CIGRE brochure 537 says a spray angle of 30° from vertical is commonly used.

Looking at your drawing, oil from the radiator could spray outside the bund. You might also want to consider maintenance access e.g. to fix leaks on the radiator or to touch up paint/galv on the stand for the radiator.
 
Last edited:
Hello 082399,
if I remember correctly, IEEE standard 980 recommends that the oil pit extends at least 1,500 mm beyond any part of the equipment filled with oil.
IEC 61936-1 reccomends instead that the length and width of the oil pit be at least equal to the length and width of the oil-filled part of the transformer plus 20% of the distance between the highest point of the transformer (including the conservator) and the upper level of the containment on each side.
As told by ema157, a 30° angle is a reasonable choice.
 