emadshaaban1
Electrical
- Jul 2, 2015
- 15
Hello
Step-down transformer (20kv /6.6KV ) 22MVA CT ration 2000/1, was tripped by (Sepam 2000) differential Protection Unit .
I've measured the Transformer insulation resistance for both primary and secondary side ,all results was great 7 G-ohm.
I've primary injected current in CTs ,all CT secondary currents was correct as ratio .
IF i have restored the Transformer with out load it keeps energized with out trip .
If I have restored the Transformer with load it take 1day and trip by differential unit .
what would the problem be? How can I full be sure the CT are okay ?
Emad Shaaban
Tripoli Libya
Step-down transformer (20kv /6.6KV ) 22MVA CT ration 2000/1, was tripped by (Sepam 2000) differential Protection Unit .
I've measured the Transformer insulation resistance for both primary and secondary side ,all results was great 7 G-ohm.
I've primary injected current in CTs ,all CT secondary currents was correct as ratio .
IF i have restored the Transformer with out load it keeps energized with out trip .
If I have restored the Transformer with load it take 1day and trip by differential unit .
what would the problem be? How can I full be sure the CT are okay ?
Emad Shaaban
Tripoli Libya