pwrengrds
Electrical
- Mar 11, 2002
- 233
What are the best practices for settings the fan control temperatures on a 50-100 MVA, 65C rise, ONAN/ONAF/ONAF, mineral oil transformer? What temperatures should the fans be set to operate at?
Usually I have seen 65C/75C or 75C/85C. We are in process of startup and the manufacture is recommending 90C/95C.
The trips are also a bit higher than I normally see. Top oil is alarming at 100C, trip at 110C, Winding alarming at 120C, trip at 130C.
David
Usually I have seen 65C/75C or 75C/85C. We are in process of startup and the manufacture is recommending 90C/95C.
The trips are also a bit higher than I normally see. Top oil is alarming at 100C, trip at 110C, Winding alarming at 120C, trip at 130C.
David