We have a transformer fault on a 33kV/6kV secondary linkbox of a 15MVA transformer.
The event recorder at the differential protection (using GE multilin 745) shows that the secondary CTs shows about 4000A (not the same value for all 3 pahses but about 4000A while the primary CTs shows about 1750A (not the same value for all 3 pahses but about 1750A).
If we use these values to estimate, a total outzone fault should have caused a secondary CTs to measure about 9625A (1750 X 5.5). Since this transformer measures 4000A at the secondary side, there seems to us that there is also an inzone fault besides outzone fault at all 3 phases. In addition, this transformer have a 8.2% impedence and by calculation, a fault could have caused a 17000A fault current. This suggest that the fault is a higher impedence fault than true fault.
Finally , this linkbox is certainly ingressed by moisture as we can see a lot of rust inside the linkbox. The windings of the transformer wasn't damaged too.
I'd like to ask if the above analysis is correct? Also, what could be the likelihood of the cause of this kind of failure (both inzone and outzone fault occurs at the same time? Could it have been moisture? If there's high humidity in the linkbox, could it have caused a flashover allover?
I find it difficult to explain the coincidence of fault happening before and after the secondary CTs and at all 3 phases.
Thanks.
The event recorder at the differential protection (using GE multilin 745) shows that the secondary CTs shows about 4000A (not the same value for all 3 pahses but about 4000A while the primary CTs shows about 1750A (not the same value for all 3 pahses but about 1750A).
If we use these values to estimate, a total outzone fault should have caused a secondary CTs to measure about 9625A (1750 X 5.5). Since this transformer measures 4000A at the secondary side, there seems to us that there is also an inzone fault besides outzone fault at all 3 phases. In addition, this transformer have a 8.2% impedence and by calculation, a fault could have caused a 17000A fault current. This suggest that the fault is a higher impedence fault than true fault.
Finally , this linkbox is certainly ingressed by moisture as we can see a lot of rust inside the linkbox. The windings of the transformer wasn't damaged too.
I'd like to ask if the above analysis is correct? Also, what could be the likelihood of the cause of this kind of failure (both inzone and outzone fault occurs at the same time? Could it have been moisture? If there's high humidity in the linkbox, could it have caused a flashover allover?
I find it difficult to explain the coincidence of fault happening before and after the secondary CTs and at all 3 phases.