Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations SDETERS on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Transformer fire detection -

Status
Not open for further replies.

helpyou

Automotive
Sep 26, 2011
79
Hello

In some transformer yards, I have seen flame detectors installed for transformer fire detection, and in some yards , heat detectors are installed. Why such a difference? I was told heat detectors are more suitable. Does it mean that flame detectors is a wrong engineering decision..

Your comments please
 
Replies continue below

Recommended for you

Heat detectors are kept close to the transformer to sense for fire protection specific to transformer. These detectors trigger Mulsifyer system that blankets the transformer cutting-off oxygen and thus helping in extinguishing fire.
Flame detectors - I have not seen used for transformers.
 
I'd say using flame detectors are not proactive. Heat detectors give ample time to take corrective actions as to what caused the elevated temperatures. Even before a fire starts.
 
I've only seen heat detectors triggering what we used to call 'fog nozzles' that cool the fire to extinguish... I don't know if they have foam monitors that encapsulate the transformer in fire suppression 'foam'. There are likely more correct terms.

Rather than think climate change and the corona virus as science, think of it as the wrath of God. Do you feel any better?

-Dik
 