MechProjectEng
Mechanical
- Jul 6, 2012
- 31
Hi all,
Hoping for some advice:
We have a recently constructed substation. The substation is a stand alone and unmanned building consisting of 3 rooms: HV Switchgear Room, LV Switchgear Room and Transformer Room. Overal size of substation is 25m x 10m. Concrete frame building.
Two walls of the transformer room are exterior walls of the substation. These walls have cluster block/air brick blockwork, and the doors to exterior are wire mesh gates. I.e. the transformer rooms are naturally ventilated, and are effectively open to the external environment. The other two walls (between transformer room and HV/LV switchgear rooms) have 2 hour fire resistance, and there is also a concrete roof slab overhead.
The transformer room houses two (2) 1250kVA transformers and one 2500kV transformer. All are oil filled with mineral oil. There are no separation walls between the transformers.
It seems our designer had not fully considered the code requirements, and as the substation has already been constructed, our AHJ has provided us with the following options:
-Add a deluge system.
-Replace the mineral oil with an approved 'less flammable' oil.
Both options are problematic for us.
The deluge system option has a fairly major problem of drainage, due to some cable trenches which link the transformer room to the switchgear rooms, which would be practically very difficult to seal to prevent flooding.
The implication of changing the transformer oil is that the transformers may have to be de-rated, having electrical implications on our process, and the other problem is that the transformers apparently have to be shipped back to the factory (overseas) to have the oil replaced and be re-tested.
I would appreciate any comments you may have, including:
-The code requirements for our particular type of installation; stand alone substation, unmanned etc. Does the code actually require a deluge system in this situation?
-Does anyone have any alternative options/ideas which we could discuss with our AHJ.
Thanks in advance.
Hoping for some advice:
We have a recently constructed substation. The substation is a stand alone and unmanned building consisting of 3 rooms: HV Switchgear Room, LV Switchgear Room and Transformer Room. Overal size of substation is 25m x 10m. Concrete frame building.
Two walls of the transformer room are exterior walls of the substation. These walls have cluster block/air brick blockwork, and the doors to exterior are wire mesh gates. I.e. the transformer rooms are naturally ventilated, and are effectively open to the external environment. The other two walls (between transformer room and HV/LV switchgear rooms) have 2 hour fire resistance, and there is also a concrete roof slab overhead.
The transformer room houses two (2) 1250kVA transformers and one 2500kV transformer. All are oil filled with mineral oil. There are no separation walls between the transformers.
It seems our designer had not fully considered the code requirements, and as the substation has already been constructed, our AHJ has provided us with the following options:
-Add a deluge system.
-Replace the mineral oil with an approved 'less flammable' oil.
Both options are problematic for us.
The deluge system option has a fairly major problem of drainage, due to some cable trenches which link the transformer room to the switchgear rooms, which would be practically very difficult to seal to prevent flooding.
The implication of changing the transformer oil is that the transformers may have to be de-rated, having electrical implications on our process, and the other problem is that the transformers apparently have to be shipped back to the factory (overseas) to have the oil replaced and be re-tested.
I would appreciate any comments you may have, including:
-The code requirements for our particular type of installation; stand alone substation, unmanned etc. Does the code actually require a deluge system in this situation?
-Does anyone have any alternative options/ideas which we could discuss with our AHJ.
Thanks in advance.