markjp
Electrical
- May 28, 2007
- 13
Hi, we are purchasing a transformer and would like some help if possible on deciding whether the transformer should be equipped with an earth screen between the HV and LV windings. The transformer is a conventional 2MVA 11kV/690V Dyn11 unit which will be used to power an MCC switchboard which has two 630kW VFDs. We have specified to the transformer vendor that the transformer needs to be suitable for the VFD duties and they have offered as an option an earth screen between the HV and LV windings to apparently help reduce effects from voltage spikes and RFI generated by the VFDs getting back on the 11kV network. The additional cost for the earth screen is approx $3,000 which isn't great in the scheme of the whole project but I'm not sure if we really need it and also whether there is any downside to having it or if there are any issues we might need to consider during installation. The site uses a common HV/LV earthing system, so if we connect all the earths together including the transformer earth screen then are we defeating the purpose of it anyway. Appreciate any thoughts on this. Thanks in advance.