Dears,
during reading power transformer (0.71/33) kv data sheet, I found term "half crest time" which equals to 0.8 s,
the question is: what is that time and why is important?
thanks and kind regards.
 
Replies continue below

Recommended for you

I had the same question when I was reviewing datasheets.

I made an enquiry with the transformer supplier and I have attached the datasheet I received from the supplier. It seems that it is the time taken by the current to fall down to 50% of the peak inrush value and it could be used for adopting protection settings to avoid operating on inrush.

Regards
electrichie123
 
 http://files.engineering.com/getfile.aspx?folder=cc0d2bc0-0e42-476e-8bd5-a93732c52afb&file=HalfCrestTime.pdf