bhellmer
Electrical
- Jun 21, 2018
- 8
Transformer kVA, Z% and X/R are commonly available.
Proposing the following equation for transformer heat release:
kW = kVA * Z% / SQRT((X/R)2 + 1)
Is this equation legitimate?
Equation givens:
Q = X/R and thus X = Q * R
Z2 = X2 + R2
Combining given equations to eliminate X:
Z2 = (Q * R)2 + R2
Solving for R:
Z2 = (Q2 * R2) + R2
Z2 = (Q2 + 1) * R2
R2 = Z2 / (Q2 + 1)
R = Z / SQRT(Q2 + 1)
Reintroducing X/R:
R = Z / SQRT((X/R)2 + 1)
Revise equation for percents:
R% = Z% / SQRT((X/R)2 + 1)
Transformer heat release:
kW = kVA * Z% / SQRT((X/R)2 + 1)
Proposing the following equation for transformer heat release:
kW = kVA * Z% / SQRT((X/R)2 + 1)
Is this equation legitimate?
Equation givens:
Q = X/R and thus X = Q * R
Z2 = X2 + R2
Combining given equations to eliminate X:
Z2 = (Q * R)2 + R2
Solving for R:
Z2 = (Q2 * R2) + R2
Z2 = (Q2 + 1) * R2
R2 = Z2 / (Q2 + 1)
R = Z / SQRT(Q2 + 1)
Reintroducing X/R:
R = Z / SQRT((X/R)2 + 1)
Revise equation for percents:
R% = Z% / SQRT((X/R)2 + 1)
Transformer heat release:
kW = kVA * Z% / SQRT((X/R)2 + 1)