Good day,
I am new to the field of power engineering and this is my first post to eng-tips. If I have not provided enough information, then please let me know for future posts.
I have been given one line data and field information to enter into a model for a short circuit study. I came across a transformer that has the following nameplate data:
Manufacturer: Ferranti-Packard
KVA: 1500/1680
Type: LNAN 55/65 rise
Primary: 6.9/13.8kV Delta
Secondary: 600Y/347
Impedance: 5.6% at 1500KVA, 13.8kV
My line side base voltage is 6.9kV, so what is a valid impedance for the transformer if impedance is only given for 13.8kV?I figured to use the standard p.u. impedance conversion of
Znew = Zold x (Vll_old^2)/(Vll_new^2)
--> .056 x (13.8^2)/(6.9^2)
This yields: Z% = 22.4%
Have I performed this calculation correctly or is there a different method to apply to transformers with multiple line side voltage options?
Thanks for the help,
Tim
KVA: 1500/1680
Secondary: 600Y/347
Tim