Transformer impedance test calculations
Mondy
GB
Hi All
Can anyone help me with the calculations involved in a transformer short circuit impedance test. I have the following data:
Transformer rated voltage =230v
Transformer rated power = 960VA
Secondary short circuited during test
ambient temperature during test = 22 deg.C
Measured impedance voltage Ez = 3.55v at 50% of rated current and at the transformers rated frequency (50Hz)
Supplied current = 2.188 average amps
Measured copper loss CuW = 7.51W at 50% of rated current and at the transformers rated frequency (50Hz)
Impedance voltage (Ez) and Load Loss (CuW) corrected to 100% of the rated current and a reference temperature of 80deg.C resulting in:
Short circuit resistance Er = 3.84%
Short circuit impedance Ez = 3.87%
Short circuit reactance Ex = 0.51%
Copper Loss CuW @ 100% load = 36.84W
I assume that the Ez of 3.84% is calculated from the 3.55v @ 50% of rated current (although I cannot get it to add up) and then the reactance Ex = 0.51 derived from
Sqr(Ez 3.87^2 - Er 3.84^2)
and Er = 36.84W * 10 /960VA
as usual, but I cant get it to add up. Or is the Ex = 0.51 calculated and then added in quadrature to come up with the Ez = 3.87%
Can anyone get these figures to make sense as I cannot get them to correlate and I can only assume I am not taking into account something in the correction of the parameters measured at 50% of rated load to 100% rated load and 80 deg.C reference temperature?
Cheers
Ray
Glad to be of help. Sometimes it's nice just to sit down with a pencil and paper and do the calcs to prove to yourself that you still know. Let us know what the outcome of the dispute is.
If we learn from our mistakes,
I'm getting a great education!
Hey no problem, Like ScottyUK said glad to help. That's why we are here and I do hope you are able to resolve the situation.