transformer impedance

Status
Not open for further replies.

bxny

Electrical
Sep 28, 2004
26
0
0
US
For a single phase, 285MVA, generator step up transformer (which is part of a 3-phase bank), 23kV - 425kV, how do I calculate the transformer impedance at the minimum and maximum taps? The transformer has an off load tap changer on the high voltage winding.
 
Replies continue below

Recommended for you

You look at the test report and see what the impedances are at those taps. It may be linear, but it may not. There was a thread here not too long ago that you might look up.
 
bxny, just a general question. Why you need these impedance? Normally for SC calculation for distribution transformers I have been using %Z.

Is this for protection relay setting purpose?
 