Transformer incomer Pothead

Status
Not open for further replies.

Electrometrical

Electrical
Mar 3, 2011
8
We have a 13.8kV/4160V, 20MVA transformer. Incomer is connected to transformer through a pothead (a HV side cable junction box). Incoming cable is 400mm2 (PILC). Inside the box, the cable is insulated with Raychem 15KV rated heat shrink sleeves. My question is that after having heat shrink sleeves, do we need to fill the box with a filler compound (e.g. Novoid X)?
 
Replies continue below

Recommended for you

It depends on the phase-phase and phase to earth clearances available in the box to achieve the system BIL.
Regards
Marmite
 
Thanks. Do you any idea what would be phase to phase clearance as per CSA?

Moreover, at what clearance level (P-P) or (P-E), we would need an additional filler (like Novoid X)?
 