LJL
Electrical
- Nov 21, 2002
- 2
I'm trying to find a way to calculate the voltage dip when a transformer is connected to weak network.
The idea is that when a transformer is connected, it may take up to ten times the nominal current. This causes a voltage dip in the network because the generator reactances are fairly high.
There are a lot of info/softwares about calculating inrush currents and also the transformer manufacturers can always provide the inrush values. The problem is that these are usually made assuming that the network is rigid. When the network is weak, the inrush current is lower because the voltage drops right away.
I haven't been able to find any material about transformer inrush currents in weak networks. That is why I ask if anybody has seen any test results, books, articles etc. about the subject? I would be very pleased to hear about them.
It seems to be a complicated phenomena. It is obvious that the inrush current gets smaller and smaller. But it is not obvious that the voltage dip gets smaller and smaller. Actually I believe that the voltage dip is at its highest usually at the 3rd cycle. This is because the generator reactance gets higher (Xd''->Xd'->Xd) faster that the inrush current gets smaller.
The biggest problem in the calculation seems to be now that how does the generator/network X (which is time dependent) effect the inrush current.
The idea is that when a transformer is connected, it may take up to ten times the nominal current. This causes a voltage dip in the network because the generator reactances are fairly high.
There are a lot of info/softwares about calculating inrush currents and also the transformer manufacturers can always provide the inrush values. The problem is that these are usually made assuming that the network is rigid. When the network is weak, the inrush current is lower because the voltage drops right away.
I haven't been able to find any material about transformer inrush currents in weak networks. That is why I ask if anybody has seen any test results, books, articles etc. about the subject? I would be very pleased to hear about them.
It seems to be a complicated phenomena. It is obvious that the inrush current gets smaller and smaller. But it is not obvious that the voltage dip gets smaller and smaller. Actually I believe that the voltage dip is at its highest usually at the 3rd cycle. This is because the generator reactance gets higher (Xd''->Xd'->Xd) faster that the inrush current gets smaller.
The biggest problem in the calculation seems to be now that how does the generator/network X (which is time dependent) effect the inrush current.