111R
Electrical
- May 4, 2012
- 114
I typically see transformer inrush plotted as a per unit value of normal transformer FLA current on a phase TCC at a specific point, such as 0.1 seconds.
I have also come across transformer inrush current curves. So, the inrush may be plotted as 10 per unit FLA at 0.1 seconds and 2 per unit FLA at 10-20 seconds.
What does this mean in normal applications? In a worst case scenario with opening and re-closing at opposite voltage zero crossings, does it mean that the inrush will be 10 per unit for 0.1 seconds and then decay down to 2 per unit after 10-20 seconds with infinite bus? Or, does it mean that if system fault current is limited to less than 10 per unit, the inrush will take longer to dissipate?
I have also come across transformer inrush current curves. So, the inrush may be plotted as 10 per unit FLA at 0.1 seconds and 2 per unit FLA at 10-20 seconds.
What does this mean in normal applications? In a worst case scenario with opening and re-closing at opposite voltage zero crossings, does it mean that the inrush will be 10 per unit for 0.1 seconds and then decay down to 2 per unit after 10-20 seconds with infinite bus? Or, does it mean that if system fault current is limited to less than 10 per unit, the inrush will take longer to dissipate?