I have never run into this scenario before so I thought I would double check:
I have a 2400V service that feeds a Delta Delta 2000KVA 2400V/12470V step up transformer that is connected in series directly to a Delta Wye 1500KVA 12470/4160V transformer (This was done this way due to transformer availability and is a temporary installation.)
Since I will be energizing both transformers at the same time will I still assume I will only see the inrush of the first transformer only at the primary of 2400V/12470V? I am making sure the fusing is sized properly and it is sized only for the 2000KVA 2400V/12470V.