Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Transformer Isolations Query

Status
Not open for further replies.

hallmg

Electrical
Aug 12, 2016
19
Hello,

The query i have is when performing isolations on transformers, why is the transformer secondary breaker opened first?

Any help would be much appreciated.

Regards,
Hallmg.
 
Replies continue below

Recommended for you

Mainly to prevent any back-feeds from the LV system appearing on the HV "Circuit" side when carrying out the HV isolation.
 
Opening the secondary first take the load off the transformer so the primary breaker has only to interrupt no-load current.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
Hi,

Thank you very much for the advice.

Hallmg.
 