Hello everyone,
I read a thread here before, which said utility fault level was given, and utility connects to the high side of a transformer, nameplate information is 20 MVA, 8.2%, 161:13kV, asked how to calculate the transformer low side fault current...below was the solution in that thread
To solve this problem you have to know the utility (source) 3-phase fault current or MVA. Assume that the source 3-phase fault is 2500 MVA. Then use the transformer MVA as the MVA base.
1) Source (utility) p.u. impedance = MVA base/SC MVA source = 20/2500 = 0.008.
2) Transformer p.u. impedance = 8.2/100 = 0.082
3) Total Zp.u. = 0.008 + 0.082 = 0.090
4) Transformer Secondary fault current = I(secondary)/ total Zp.u.
5) Transformer secondary current = 20 MVA x 1000/(1.73 x13 kV) = 889.28 Amps.
6) Transformer fault current at 13 kV side = 889.28/0.090 = 9,880 Amps.
my question is what the type of this transformer fault current at low side? is it a LG, or LL, or LLG or LLL or LLLG fault? or this 9880 amp is just the highest one, doesn't matter which type of the fault?
Thank you
Thank you