Transformer modelling for switching transient

Status
Not open for further replies.

Adam1980

Electrical
Feb 17, 2012
87
Dear all,

I am doing a transient study for which the transofmer data from the manufacturer is not easy to provide.

Concerning that issue i have two questions:
1- are there any recommended values of the transformer capacitances (transformer is 40 MVA YYN0 132/33 kV). I will be calculating switching transients (slow front) but may also consider fast fronts for re-strikes. Would considering/neglecting the capacitances affect the calculations?
There are some proposed values from not so official sources but with quite a large range (IEEE industrial applications society magazine).
2- would the phase shift of the transformer affect the calculations? I have an inverter transformer with a phase shift of 10°. This is not available from the model.

Thank you.
 
Replies continue below

Recommended for you

Adam,
as regards the influence of transformer capacitance on switching transients, it depends on where the circuit breaker is: if you are simulating transformer switching-off transient the effect of its capacitance is not negligible; the same applies if you are studing a phenomenon that could involve the transformer itself (i.e. transformer-terminated lines or energization of lines through a transformer). If you are performing a switching transient study on a large network, the effect is much less important.
As regards phase shift it could be more important for harmonic studies rather than fast transients ones