Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations IDS on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Transformer Noise 1

Status
Not open for further replies.

SidiropoulosM

Electrical
Nov 25, 2002
144
Any ideas on reducing noise from a 230/115 kv transformer without reducing operating voltage? The noise occurs when the transformer operates at 107% nominal voltage.
 
Replies continue below

Recommended for you


Likely the NLTC has been set for highest ratio? [I have no immediate reference, but ISTR acoustical noise roughly increases with the square of voltage. 1.07 puV <> 1.145 pu noise]
 
Busbar, thanks for your comment. You're right on, we can solve the problem by changing the NLTC position, but not on this transformer, on an upstream 500/230 kv transformer. This is probably what we'll end up doing. This will effectively reduce the operating voltage at the 230 kv bus, which will have some drawbacks during peak load conditions. I was asking for ideas on solving the problem without changing the voltage, which may not be possible.
 

Looked through the online IEEE T-PWRD index, and only found material on transformer acoustic measurement techniques, not mitigation—short of noise cancellation by active means. The V² r&#8729;o&#8729;t is from an associate that has considerable power-transformer experience.

[CIGRE shows some interesting titles, but no online access to text here.]
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor