Apr 2, 2024 #1 gago03 Electrical Apr 2, 2024 1 0 0 DZ hey ; after transformer oil degassing operation , should i measure the winding resistance insulation ? if yes what the standar
hey ; after transformer oil degassing operation , should i measure the winding resistance insulation ? if yes what the standar
Apr 4, 2024 #2 prc Electrical Aug 18, 2001 1,998 0 36 IN It's not necessary. If you opened any current path or operated a tap-changer to wipe the contacts, then only winding resistance measurements need to be repeated. Upvote 0 Downvote
It's not necessary. If you opened any current path or operated a tap-changer to wipe the contacts, then only winding resistance measurements need to be repeated.