Hi Gurus,
I have heard conflicting opinions on selecting a Transformer OCP device rating. Problem is while CEC 26-26(2b) stipulates conductor size on Secondary side shall have ampacity rating of not less than 125% of rated Secondary current, some in my team are applying same rule to transformers OCP devices, and it seems confusing to me.
Proposal 1: assume a 45kVA 3ph 600v/208v step down transformer
Primary current = 45x1000/ 600 x 1.73 = 43A
125% Pcurrent = 54A, Hence a 60A Overcurrent device on Primary should be chosen.
Secondary current = 45x1000/ 208 x 1.73 = 125A
125% of Full load current = 156A , Panel higher rating = 200A
Proposal 2: assume a 35kVA 3ph 600v/208v step down transformer
Primary current = 35x1000/ 600 x 1.73 = 33A
125% Pcurrent = 42A, Hence a 50A OCP device.
Secondary current = 35x1000/ 208 x 1.73 = 97A
125% of Full load current = 121A , hence a 150A CB Panel on the secondary side should be chosen.
Option 1: Choose the 45kVA, Since the primary side has a 60A fuse already, a 100A CB panel and #2/0 AWG Cu cable on secondary side would suffice
Option 2: Nope! with a 45kVA transformer, CB must be upgraded to match next higher rating of full load secondary current (i.e 150A CB).
Option 3: Choose 35kVA instead, since breaker's 'Mains Rating' is 125A.
Option 1 and 3 makes more sense to me as per 26-254. Your thoughts pls?
I have heard conflicting opinions on selecting a Transformer OCP device rating. Problem is while CEC 26-26(2b) stipulates conductor size on Secondary side shall have ampacity rating of not less than 125% of rated Secondary current, some in my team are applying same rule to transformers OCP devices, and it seems confusing to me.
Proposal 1: assume a 45kVA 3ph 600v/208v step down transformer
Primary current = 45x1000/ 600 x 1.73 = 43A
125% Pcurrent = 54A, Hence a 60A Overcurrent device on Primary should be chosen.
Secondary current = 45x1000/ 208 x 1.73 = 125A
125% of Full load current = 156A , Panel higher rating = 200A
Proposal 2: assume a 35kVA 3ph 600v/208v step down transformer
Primary current = 35x1000/ 600 x 1.73 = 33A
125% Pcurrent = 42A, Hence a 50A OCP device.
Secondary current = 35x1000/ 208 x 1.73 = 97A
125% of Full load current = 121A , hence a 150A CB Panel on the secondary side should be chosen.
Option 1: Choose the 45kVA, Since the primary side has a 60A fuse already, a 100A CB panel and #2/0 AWG Cu cable on secondary side would suffice
Option 2: Nope! with a 45kVA transformer, CB must be upgraded to match next higher rating of full load secondary current (i.e 150A CB).
Option 3: Choose 35kVA instead, since breaker's 'Mains Rating' is 125A.
Option 1 and 3 makes more sense to me as per 26-254. Your thoughts pls?