The site is provided with 100% back-up generator power. After working fine for 6 months last Friday there was a power failure. The open transition ATS energized the generator and closed to it without a problem. On utility power return, the circuit breaker supplying a 150kVA transformer tripped as did the panelboard’s main circuit breaker as well as the switchboard’s electronic circuit breaker supplying the panelboard.
The system is a temporary arrangement where one small out building is operating while the main building is under construction. As such the main circuit breakers are rated 250A, and the circuit breaker supplying the transformer is 200A. The site is also in Canada so the primary voltage is 600V.
The outbuilding will house racks of electronic equipment, which are currently being set-up, so the electrical load very light. The problem appears to be transformer in rush (although, I'm open to other suggestions).
Does anyone have any suggestions on the best way to reduce in rush? We have considered putting a false load on the transformer, but that seem inelegant and hard to justify to the owner. The problem seems to be similar to motor in rush where capacitance banks have been used to dampen the in rush. Does anyone have any experience with this or other suggestions?
The system is a temporary arrangement where one small out building is operating while the main building is under construction. As such the main circuit breakers are rated 250A, and the circuit breaker supplying the transformer is 200A. The site is also in Canada so the primary voltage is 600V.
The outbuilding will house racks of electronic equipment, which are currently being set-up, so the electrical load very light. The problem appears to be transformer in rush (although, I'm open to other suggestions).
Does anyone have any suggestions on the best way to reduce in rush? We have considered putting a false load on the transformer, but that seem inelegant and hard to justify to the owner. The problem seems to be similar to motor in rush where capacitance banks have been used to dampen the in rush. Does anyone have any experience with this or other suggestions?