I believe that NEC Article 450.3 Overcurrent Protection (and Table 450.3) directly determines the secondary side breaker sizing (and bus sizing).
For example, if I have a 2500kVA, 13.8-0.48kV Transformer, the rated secondary side current is 3007A. As per Table 450.3, for 480V secondary (<1000V), the breaker maximum rating or setting shall be 125% of Transformer rated current i.e 3007 x 1.25 = 3759A. The closest standard rating is 4000A. Thus breaker and bus rating on secondary side MCC shall be 4000A each.
So far so good.
Now let us say that this Transformer is rated at 30degC and undergoes a derating for 50degC ambient.
As per IEEE C57.91 Guide for Loading Mineral-Oil-Immersed Transformers and Step-Voltage Regulators’, Section 6, the derating shall be 1.5% for each degree rise above 30degC (ONAN only).
Thus for 50degC ambient i.e 20degC rise, the derating shall be 20 x 1.5 = 30%.
Thus the derated kVA of the Transformer shall be 2500 x 0.7 = 1750kVA. The corresponding current is 2105A.
Going back to NEC Article 450.3 requirement, max. secondary side breaker rating or setting shall be 2105 x 1.25 = 2631A.
Closest higher standard rating or setting is 3000A. Thus both CB and bus bar can be sized at 3000A.
Is the above correct? By not following the nameplate Transfrmer rating but following the derated rating, am I flouting NEC requirement?
For example, if I have a 2500kVA, 13.8-0.48kV Transformer, the rated secondary side current is 3007A. As per Table 450.3, for 480V secondary (<1000V), the breaker maximum rating or setting shall be 125% of Transformer rated current i.e 3007 x 1.25 = 3759A. The closest standard rating is 4000A. Thus breaker and bus rating on secondary side MCC shall be 4000A each.
So far so good.
Now let us say that this Transformer is rated at 30degC and undergoes a derating for 50degC ambient.
As per IEEE C57.91 Guide for Loading Mineral-Oil-Immersed Transformers and Step-Voltage Regulators’, Section 6, the derating shall be 1.5% for each degree rise above 30degC (ONAN only).
Thus for 50degC ambient i.e 20degC rise, the derating shall be 20 x 1.5 = 30%.
Thus the derated kVA of the Transformer shall be 2500 x 0.7 = 1750kVA. The corresponding current is 2105A.
Going back to NEC Article 450.3 requirement, max. secondary side breaker rating or setting shall be 2105 x 1.25 = 2631A.
Closest higher standard rating or setting is 3000A. Thus both CB and bus bar can be sized at 3000A.
Is the above correct? By not following the nameplate Transfrmer rating but following the derated rating, am I flouting NEC requirement?