Humble2000
Electrical
- Nov 17, 2005
- 132
a 750KVA ANN transformer secondary side breaker is ordered with a 1000AMp LTP and fixed LTD . This is 1.4 times more than Tx FLA at 600V. Breaker is rated for 100% rated name plate operation.
Two issues is first the primary S&C fuse at 25KV does not coordinate with a 25 AMp fuse ( they touch at LTD) and the bigger size would violate the ESA ruels for more than 1.5 times of primary amps.
Does the consulatnt pick a wrong size breaker?
I dont think the breaker would provide adequate transformer protection with that size breaker.
Two issues is first the primary S&C fuse at 25KV does not coordinate with a 25 AMp fuse ( they touch at LTD) and the bigger size would violate the ESA ruels for more than 1.5 times of primary amps.
Does the consulatnt pick a wrong size breaker?
I dont think the breaker would provide adequate transformer protection with that size breaker.