I am looking into adjusting a tap on your 110MVA Main step up transformer. I know the voltages are a direct correlation to the turn ratios. The issue we are having is the voltage on the low-side is getting to high, forcing inverters to trip since they are out of their voltage operating range. The Tap is currently set to neutral. It is a automatic load tap transformer however we are having issues with the automatic adjustments, therefore will set to a single tap setting.
What else should i look at inorder to determine the optimal tap setting. I have low side and high side voltages for the past week but are there any other equations that will fine tune my selection besides Vp/Vs = turns ratio = corresponding tap setting?
I am looking into adjusting a tap on your 110MVA Main step up transformer. I know the voltages are a direct correlation to the turn ratios. The issue we are having is the voltage on the low-side is getting to high, forcing inverters to trip since they are out of their voltage operating range. The Tap is currently set to neutral. It is a automatic load tap transformer however we are having issues with the automatic adjustments, therefore will set to a single tap setting.
What else should i look at inorder to determine the optimal tap setting. I have low side and high side voltages for the past week but are there any other equations that will fine tune my selection besides Vp/Vs = turns ratio = corresponding tap setting?