We have a transformer supplied by a manufacturer which is planned to be installed within a room. The transformer is manufactured to IEC60076 standards.
The question is regarding the ventilation design for the room. IEC60076 states that the cooling air temperature has to be within 40 degrees. The manufacturer has provided a formula for sizing the ventilation fans, etc. We have an engineer who states that as long as we circulate air in and out of the room at the rate of flow of air specified by the manufacturer and the air inflow is within 40 degrees, we satisfy the needs of the transformer and the standard.
However, my problem is that the ventilation sizing is all designed for a change in temperature (between inlet and outlet from the room) of 10 degrees. Therefore, if the temperature on a day is 35 degres, the ventilation system will make sure that the outlet temperature is 45 degrees and it will allow a 10 degree rise in temperature within the room. This means that the transformer will be sitting in an ambient temperature above 40 degrees. I do not think IEC 60076 standard allows the transformer to sit in an ambient temperature above 40 degrees. The reason why I say so is that I believe the winding hot spot temperatures and ratings are all calculated based on the transformer placed in an ambient temperature of 40 degrees and not higher. Therefore, I am saying that the room requires cooling (air conditioners), not just fans.
Can others pls comment on this issue?
The question is regarding the ventilation design for the room. IEC60076 states that the cooling air temperature has to be within 40 degrees. The manufacturer has provided a formula for sizing the ventilation fans, etc. We have an engineer who states that as long as we circulate air in and out of the room at the rate of flow of air specified by the manufacturer and the air inflow is within 40 degrees, we satisfy the needs of the transformer and the standard.
However, my problem is that the ventilation sizing is all designed for a change in temperature (between inlet and outlet from the room) of 10 degrees. Therefore, if the temperature on a day is 35 degres, the ventilation system will make sure that the outlet temperature is 45 degrees and it will allow a 10 degree rise in temperature within the room. This means that the transformer will be sitting in an ambient temperature above 40 degrees. I do not think IEC 60076 standard allows the transformer to sit in an ambient temperature above 40 degrees. The reason why I say so is that I believe the winding hot spot temperatures and ratings are all calculated based on the transformer placed in an ambient temperature of 40 degrees and not higher. Therefore, I am saying that the room requires cooling (air conditioners), not just fans.
Can others pls comment on this issue?