Transformer's Theory question 2
mackmaster
8
CA
I have difficulty to understand the theory of how the transformer acually works and have a question regarding to that:
The primary winding of a transformer consists of two parts:
1- Primary leakage inductance Lp1
2-Primary coupling inductance L1
neglect the wiring resistance.
So the total primary inductance Lp=Lp1 + L1
The voltage across L1 must be constnat all the time = N1*d@m/dt
where @m is the mutual magnetizing flux, which is constant for all loads.
Now,if the primary is connected into a constant AC supply voltage V1 and the secondary is connected into resistive load,then:
V1 = Lp1*d i1/dt + N1*d@m/dt
V1 and N1*d@m/dt are constants while the first term of the equation Lp1*d i1/dt
is variable depends on the primary current !
Any one can explain that conflict in the equation ?
mackmaster,
Primary impedance changes the amount of voltage drop depending on the load current (VD= I[sub]L[/sub] x Z[sub]p[/sub]). Since I[sub]m[/sub] is a function of E[sub]m[/sub] (magnetizing voltage= V[sub]supply[/sub] - VD), a bigger load current creates a larger VD, and therefore a lesser E[sub]m[/sub]! I[sub]m[/sub] changes with load current!
Crystal!