Engcan
Electrical
- Dec 11, 2005
- 23
Hi Everybody
Me and my sr. engineer during a discussion did not agree on a fundamental law, and I beleive he is correct. But
I need a final word from you guys. Plz analyze the situation below.
A 13.8 KV line is feeding two transformers in a building.
I am not sure of the %Z of the two transformers but I know they are 13.8Kv/600V. Now they are connected on to one switchgear which has a split bus arrangement that means
bus A and bus B. I beleive each T/F is feeding one bus.
One T/f is for lighting load and IT server rooms and the other one is for HVAC load. We want to run two risers on
10 th floor. I suggested that as we have one transfer switch, we can connect both risers to a single bus and use it as a normal supply. But he said no, I am not sure why.
I think this is paralleling of transformers what my concern is if we do it what is the problem?. As both trms are fed from same local utility, we can use this as a normal supply bus(this new connected bus) and another load bus, on which both HVAC and lighting loads will be connected and one transfer switch will be enough otherwise we need two transfer switches. I spoke to some body in local utility he said they use network transformers for this kind of arrangement and this setting is not usual in buildings. Please advise, Is this not possible, if yes what are the implications.
Thanks
Me and my sr. engineer during a discussion did not agree on a fundamental law, and I beleive he is correct. But
I need a final word from you guys. Plz analyze the situation below.
A 13.8 KV line is feeding two transformers in a building.
I am not sure of the %Z of the two transformers but I know they are 13.8Kv/600V. Now they are connected on to one switchgear which has a split bus arrangement that means
bus A and bus B. I beleive each T/F is feeding one bus.
One T/f is for lighting load and IT server rooms and the other one is for HVAC load. We want to run two risers on
10 th floor. I suggested that as we have one transfer switch, we can connect both risers to a single bus and use it as a normal supply. But he said no, I am not sure why.
I think this is paralleling of transformers what my concern is if we do it what is the problem?. As both trms are fed from same local utility, we can use this as a normal supply bus(this new connected bus) and another load bus, on which both HVAC and lighting loads will be connected and one transfer switch will be enough otherwise we need two transfer switches. I spoke to some body in local utility he said they use network transformers for this kind of arrangement and this setting is not usual in buildings. Please advise, Is this not possible, if yes what are the implications.
Thanks