muncher
Structural
- Aug 29, 2010
- 8
I have consulted with other "very-experienced" structural engineers (design and plan check) to determine precisely what triggers revisions to a lateral load-resisting system under the provisions of IBC 3404.4 (2012, 2009, etc) and read the code slightly differently. I am hoping to get a wider range of interpretation via this forum. (For those respondents, please indicate your interpretation of the code language - not just what you've done in the past.)
As an example, for a simple project that requires a solitary 10'-long shear wall to be reduced by 6" due to an enlarged opening, here is my thought process...
Considering the triggers:
"...where the alteration increases design lateral loads in accordance with Section 1609 or 1613..." [not applicable as no new exposure for wind or weight for seismic increases]
"...where the alteration results in a structural irregularity as defined in ASCE 7..." [presume that this does not apply]
"...where the alteration decreases the capacity of any existing lateral load-carrying structural element..." [this applies as the 9.5'-long wall has less capacity than the 10'-long]
Therefore,...
"the structure of the altered building or structure shall be shown to meet the requirements of Sections 1609 and 1613".
However, an exception exists stating...
"Any existing lateral load-carrying structural element whose demand-capacity ratio with the alteration considered is not more than 10 percent greater than its demand-capacity ratio with the alteration ignored shall be permitted to remain unaltered.
At a glance, this seems like we might be ok as we've only reduced the wall's capacity by 5% (= 6"/10'); however, the next statement clarifies the term "demand-capacity ratio"...
"For purposes of calculating demand-capacity ratios, the demand shall consider applicable load combinations with design lateral loads or forces per Sections 1609 and 1613"
To me, this seems to indicate that the analysis must always be done and, in this step, the engineer must determine the demand based on CURRENT code provisions and this is the problem. Many of us are aware that the evolution of the codes have had significant impact on the lateral loads that we must impart on structures in the design phase. Just the fact that the "newly-determined" lateral loads may be higher than those used in the initial design of the structure (many years ago?) could trigger the need for the addition of supplemental support with ANY capacity reduction, no matter how slight, of the existing wall.
There is NO allowance for the "belief" that "because the wall is still there it must indicate that it's historical demand-capacity ratio must be a maximum of 1" (which would then allow our 5% reduction to be less than the code-allowed 10%).
As an example, for a simple project that requires a solitary 10'-long shear wall to be reduced by 6" due to an enlarged opening, here is my thought process...
Considering the triggers:
"...where the alteration increases design lateral loads in accordance with Section 1609 or 1613..." [not applicable as no new exposure for wind or weight for seismic increases]
"...where the alteration results in a structural irregularity as defined in ASCE 7..." [presume that this does not apply]
"...where the alteration decreases the capacity of any existing lateral load-carrying structural element..." [this applies as the 9.5'-long wall has less capacity than the 10'-long]
Therefore,...
"the structure of the altered building or structure shall be shown to meet the requirements of Sections 1609 and 1613".
However, an exception exists stating...
"Any existing lateral load-carrying structural element whose demand-capacity ratio with the alteration considered is not more than 10 percent greater than its demand-capacity ratio with the alteration ignored shall be permitted to remain unaltered.
At a glance, this seems like we might be ok as we've only reduced the wall's capacity by 5% (= 6"/10'); however, the next statement clarifies the term "demand-capacity ratio"...
"For purposes of calculating demand-capacity ratios, the demand shall consider applicable load combinations with design lateral loads or forces per Sections 1609 and 1613"
To me, this seems to indicate that the analysis must always be done and, in this step, the engineer must determine the demand based on CURRENT code provisions and this is the problem. Many of us are aware that the evolution of the codes have had significant impact on the lateral loads that we must impart on structures in the design phase. Just the fact that the "newly-determined" lateral loads may be higher than those used in the initial design of the structure (many years ago?) could trigger the need for the addition of supplemental support with ANY capacity reduction, no matter how slight, of the existing wall.
There is NO allowance for the "belief" that "because the wall is still there it must indicate that it's historical demand-capacity ratio must be a maximum of 1" (which would then allow our 5% reduction to be less than the code-allowed 10%).