Trip cause in ABB Relay REF615

Status
Not open for further replies.

SA07

Electrical
Feb 22, 2018
365
0
0
MU
Hi
Is there a way to identify the event/disturbance/record data when the relay ABB REF615 trips?
For comparison, relay SEL 311, 387, in the events recorded we can see a T next to the event meaning the relay has tripped.
In the ABB, we do not see the same thing. Plz see attached a doc with some print screens to explain my point.
We want to identify the cause of a trip in the ABB relay whether UV, OC, EF, etc. We see many events, disturbances recorded in the relay ABB.

Thanks
 
 https://files.engineering.com/getfile.aspx?folder=fef7a2ab-5db8-406a-b075-7c3cd18b8226&file=Eng_Tips_Trip_record_in_ABB_Relay_REF615.docx
Replies continue below

Recommended for you

Its Phase to Phase Under Voltage start. When it will trip, it will show Trip. Application configuration needs to be checked, as trip contact can be operted from start event.
 