Hi,
Have temporary 20 amp AC circuit serving no more than 700 watts of DC transformers for Fiber Optics modems. The breaker is in the center of a 3,000 ft line of #8 and #10 wire. 200 watts are at one end 1,600 ft away and 500 watts are on the other end 1,400 ft away.
Facts
-----
(1) Cable is buried in conduit
(2) All receptacles show 120+ volts
(3) Either side will run solo . . . no problem
(4) Throws 20 amp circuit breaker in box when both are attached (after about 15 minutes)
(5) All GFCI receptacles
(6) Circuit breaker sits 10 ft from 1000 AMP transformer
(7) Only panel on 1000 Amp transformer
(8) Only circuit in 200 AMP panel
(9) Both sides have 10 amp power strips which don't throw
700 watts draws far less than 20 amps so, what else could be load related that would throw the breaker? Voltage drop due to the line lengths? Does the circuit breake understand voltage drop?
Any ideas?
Thank you!
Larry
Have temporary 20 amp AC circuit serving no more than 700 watts of DC transformers for Fiber Optics modems. The breaker is in the center of a 3,000 ft line of #8 and #10 wire. 200 watts are at one end 1,600 ft away and 500 watts are on the other end 1,400 ft away.
Facts
-----
(1) Cable is buried in conduit
(2) All receptacles show 120+ volts
(3) Either side will run solo . . . no problem
(4) Throws 20 amp circuit breaker in box when both are attached (after about 15 minutes)
(5) All GFCI receptacles
(6) Circuit breaker sits 10 ft from 1000 AMP transformer
(7) Only panel on 1000 Amp transformer
(8) Only circuit in 200 AMP panel
(9) Both sides have 10 amp power strips which don't throw
700 watts draws far less than 20 amps so, what else could be load related that would throw the breaker? Voltage drop due to the line lengths? Does the circuit breake understand voltage drop?
Any ideas?
Thank you!
Larry