We have a 6,6kV 6MW 6/12 pulse thyristor Mine Winder with a 3,1 MVAr 3rd order damped filter (Resistor and decoupling capacitor across the reactor) tuned at 4,8p.u. connected to the same busbar (no other loads). Acceleration of the winder peaks the load at about 15MVA.
Measurement at approx. 500 ms averaging shows normal harmonics for the winder with the filter out of circuit. With the filter in circuit acceleration of the winder results in immediate tripping of the filter on harmonics (the filter is rated for 90% harmonics at 5th).
Parallel resonance below the tuning frequency occurs at exactly 4p.u. We measured the filter harmonics during the trip and managed to see one set of readings as the winder accelerated before the filter tripped. The 4th harmonic was at around 350A on all phases (it could be and is likely, based on the levels that the relay saw, that the peak 4th is much higher).
The 4th without the filter in circuit is 4-5A giving an amplification factor of anywhere between 90 and 300.
Simulation of the network shows a max. possible amplification of 25. What on earth is going on?
Is it possible that some interaction is occuring between the filter and the winder and is it related to the lack of damping on the busbar?
In South Africa we have relatively high levels of harmonics due to the many mines and therefore are very experienced in the field of harmonics. However, this is difficult to explain - the max. amlification that we have seen in 20 years is 40x and that situation was theoretically explained.
Measurement at approx. 500 ms averaging shows normal harmonics for the winder with the filter out of circuit. With the filter in circuit acceleration of the winder results in immediate tripping of the filter on harmonics (the filter is rated for 90% harmonics at 5th).
Parallel resonance below the tuning frequency occurs at exactly 4p.u. We measured the filter harmonics during the trip and managed to see one set of readings as the winder accelerated before the filter tripped. The 4th harmonic was at around 350A on all phases (it could be and is likely, based on the levels that the relay saw, that the peak 4th is much higher).
The 4th without the filter in circuit is 4-5A giving an amplification factor of anywhere between 90 and 300.
Simulation of the network shows a max. possible amplification of 25. What on earth is going on?
Is it possible that some interaction is occuring between the filter and the winder and is it related to the lack of damping on the busbar?
In South Africa we have relatively high levels of harmonics due to the many mines and therefore are very experienced in the field of harmonics. However, this is difficult to explain - the max. amlification that we have seen in 20 years is 40x and that situation was theoretically explained.