Generator paralleling problem
Our plant has Two-2 M watt, 480 volt alternators. Scenario: Generators are paralleled via APD onto a common bus. Voltages, kwatts, kamps and frequency meters all concur.
Problem 1: The power factor meters are 180 out. Generator 1 meter is pegged to max. IND. Generator 2 at max.CAP.
Problem 2: When Load is applied it is not equally shared. kW meters are equal however kA meters are not. Gen 1 is producing more power than Gen 2
Question. What adjustments were needed? Should operating Gen. 1 be loaded, prior to bringing on incoming Gen. 2 ? And finally, what's happening with the power factor meters?