Brain picking time (with apologies for length)…….
We have a big three phase generator (BG) & a little single phase one (LG). During the day BG runs and supplies a three phase load and a critical single phase load. At night LG runs and supplies the single phase load only.
Both gens have a 30mA RCD on the output and are connected to a panel which starts the BG if LG isn’t running. Workers stop LG when they arrive (panels starts BG) and start LG when they leave (panel stops BG). If LG stops in the night then panel starts BG.
Panel gets power from both gens and, via contactors, energises a three phase and single phase output if BG is running and single phase only if LG is running. It has two control transformers (240/110), one fed from each gen, with the 0V of the secondaries tied to earth. This is the only connection between the two systems, contactors have timers to give a 20s dwell between the two single phase contactors at changeover time.
Problem we have is that when BG stops its RCD is tripping. It does it maybe 60% of the time and only if LG is running i.e. if we fiddle it so the panel only thinks LG is running then the rcd stays in.
Both gens claim to have star/neutral connected to earth
Any thoughts welcome
We have a big three phase generator (BG) & a little single phase one (LG). During the day BG runs and supplies a three phase load and a critical single phase load. At night LG runs and supplies the single phase load only.
Both gens have a 30mA RCD on the output and are connected to a panel which starts the BG if LG isn’t running. Workers stop LG when they arrive (panels starts BG) and start LG when they leave (panel stops BG). If LG stops in the night then panel starts BG.
Panel gets power from both gens and, via contactors, energises a three phase and single phase output if BG is running and single phase only if LG is running. It has two control transformers (240/110), one fed from each gen, with the 0V of the secondaries tied to earth. This is the only connection between the two systems, contactors have timers to give a 20s dwell between the two single phase contactors at changeover time.
Problem we have is that when BG stops its RCD is tripping. It does it maybe 60% of the time and only if LG is running i.e. if we fiddle it so the panel only thinks LG is running then the rcd stays in.
Both gens claim to have star/neutral connected to earth
Any thoughts welcome