Hi all,
sorry if it is a little bit off topic, but I have questions about FM 7.88.
I am designing a tank farm protection, in particular since the spacing to load/unload station from the diesel tanks is inadeguate I have to design a load/unload station protection.
In the FM 7.88, clause 2.4.2.9, it is written:
" Where spacing to rail or truck load/unload stations is inadequate (i.e., not in accordance with Section 2.2.2) provide deluge water spray (installed in accordance with DS 4-1N) for the load/unload station (vehicle
and pumps) at a rate of 0.3 gpm/ft2 (12 mm/min) of tank surface. Include water supply duration for 2 hours and at least 500 gpm (1,900 L/min) for hose streams."
So I have some question about this clause:
1) "at a rate of 0.3 gpm/ft2 (12 mm/min) of tank surface"...Which tank surface is intended in order to calculate the flow rate?
2) Do you think that make sense to protect the truck load/unload station with a deluge water spray? I do not think that only water could be effective, I think that a foam-water system is better!
sorry if it is a little bit off topic, but I have questions about FM 7.88.
I am designing a tank farm protection, in particular since the spacing to load/unload station from the diesel tanks is inadeguate I have to design a load/unload station protection.
In the FM 7.88, clause 2.4.2.9, it is written:
" Where spacing to rail or truck load/unload stations is inadequate (i.e., not in accordance with Section 2.2.2) provide deluge water spray (installed in accordance with DS 4-1N) for the load/unload station (vehicle
and pumps) at a rate of 0.3 gpm/ft2 (12 mm/min) of tank surface. Include water supply duration for 2 hours and at least 500 gpm (1,900 L/min) for hose streams."
So I have some question about this clause:
1) "at a rate of 0.3 gpm/ft2 (12 mm/min) of tank surface"...Which tank surface is intended in order to calculate the flow rate?
2) Do you think that make sense to protect the truck load/unload station with a deluge water spray? I do not think that only water could be effective, I think that a foam-water system is better!