Rbang
Mechanical
- Jan 9, 2014
- 3
Good Day All !
Although I have perused the site on many occasions and shared in the knowledge posted, this is the first time for me to request assistance.
Should I not be in the proper section , please inform me so that it may be posted accordingly. Thank You.
I have an application where I am attempting to confirm the GPM requirements of thermal fluid to convey a given amount of BTU's into a liquid.
In addition, to confirm the Surface Area and Pipe Length required to achieve the goal.
Conditions:
Liquid: Water
Weight: 8.33 lb/Gal
Volume: 10,000 Gal
Container: 8' Dia. x 28' Vertical Carbon Steel
Insulation: 3" Fiberglass
Start Temp: 70F
Ending Temp: 130F
Temp Rise : 60F
(1 BTU x 1 lb = 1 F rise in temp.)
BTU's Required: 10,000 x 8.33 x 60 = 4,998,000 BTU
Tank Heat Loss:
(K-Factor/Insulation Thickness x Surface Area x (Liquid Temp - Air Temp))
.29 / 3 x 804 x (130-60) = 5,440 BTU/Hr
Time to Heat: 4 hrs
4,998,000 BTU / 4 hrs = 1,249,500 + 5,440 = 1,254,940 BTU/Hr
Thermal Fluid Temp In: 450F
Thermal Fluid Temp Out: 425F
I have Calculated "Q" as follows:
A x Delta x U = Q
A=.622 , Delta = 337.5, U = 20
.622 x 337.5 x 20 =4,198.5 BTU per LF of 2" Sch. 40 CS Pipe
To calculate the LF of 2" Pipe required:
BTU-Hr / Q = LF
1,254,940 / 4,198.5 = 186 LF
The Thermal Fluid Properties are listed as:
Specific Heat = 0.56 Btu/Lb/F
Thermal Conductivity = .07 Btu-Ft/Ft2/Hr/F
Wt. Per Gal = 7.0
This is where I have a bit of confusion. Calculating the GPM's required.
My instincts tell me that:
For each gallon of Thermal Fluid that passes through the length of coil with a 25F Temperature drop I would lose 411.6 BTU.
Wt. per Gallon x Specific Heat x Temp Drop x Thermal Conductivity x 60 min.
7 x .56 x 25 * .07 * 60= 411.6 BTU Loss Per Gallon.
To Transfer 1,254,940 BTU's per hr.
1,254,940 / 411.6 = 3,049 GPH
3,049 GPH / 60 = 51 GPM (Could this be Correct?)
Would someone be willing to assist with a confirmation / correction and direction.
I sincerely Thank You for Sharing your Knowledge.
Rbang
Although I have perused the site on many occasions and shared in the knowledge posted, this is the first time for me to request assistance.
Should I not be in the proper section , please inform me so that it may be posted accordingly. Thank You.
I have an application where I am attempting to confirm the GPM requirements of thermal fluid to convey a given amount of BTU's into a liquid.
In addition, to confirm the Surface Area and Pipe Length required to achieve the goal.
Conditions:
Liquid: Water
Weight: 8.33 lb/Gal
Volume: 10,000 Gal
Container: 8' Dia. x 28' Vertical Carbon Steel
Insulation: 3" Fiberglass
Start Temp: 70F
Ending Temp: 130F
Temp Rise : 60F
(1 BTU x 1 lb = 1 F rise in temp.)
BTU's Required: 10,000 x 8.33 x 60 = 4,998,000 BTU
Tank Heat Loss:
(K-Factor/Insulation Thickness x Surface Area x (Liquid Temp - Air Temp))
.29 / 3 x 804 x (130-60) = 5,440 BTU/Hr
Time to Heat: 4 hrs
4,998,000 BTU / 4 hrs = 1,249,500 + 5,440 = 1,254,940 BTU/Hr
Thermal Fluid Temp In: 450F
Thermal Fluid Temp Out: 425F
I have Calculated "Q" as follows:
A x Delta x U = Q
A=.622 , Delta = 337.5, U = 20
.622 x 337.5 x 20 =4,198.5 BTU per LF of 2" Sch. 40 CS Pipe
To calculate the LF of 2" Pipe required:
BTU-Hr / Q = LF
1,254,940 / 4,198.5 = 186 LF
The Thermal Fluid Properties are listed as:
Specific Heat = 0.56 Btu/Lb/F
Thermal Conductivity = .07 Btu-Ft/Ft2/Hr/F
Wt. Per Gal = 7.0
This is where I have a bit of confusion. Calculating the GPM's required.
My instincts tell me that:
For each gallon of Thermal Fluid that passes through the length of coil with a 25F Temperature drop I would lose 411.6 BTU.
Wt. per Gallon x Specific Heat x Temp Drop x Thermal Conductivity x 60 min.
7 x .56 x 25 * .07 * 60= 411.6 BTU Loss Per Gallon.
To Transfer 1,254,940 BTU's per hr.
1,254,940 / 411.6 = 3,049 GPH
3,049 GPH / 60 = 51 GPM (Could this be Correct?)
Would someone be willing to assist with a confirmation / correction and direction.
I sincerely Thank You for Sharing your Knowledge.
Rbang