Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations GregLocock on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Tube Supports Temperature Design of Fired Heaters

Status
Not open for further replies.

Wrl69

Mechanical
Oct 2, 2003
18
We have to modify convection section in two fired heaters (oil refinery), to obtain a determined (by customer) outlet fuel gas temperature. So we have the following questions:

1. On their condictions, the shield section tube supports temperature design will be 2098°F; it is over API 560 indication (2000°F). What can we do? What material of tube supports is recomended on that temperature?

2. What can we do, if flue gas temperature gradient across a single convection intermediate tube support is over 400°F, indicated by API 560? In our case we have one case with 844°F and other case with 506°F.

Thanks,
 
Replies continue below

Recommended for you

WRL69,
One way of getting over the temperature gradient limitation would be to simply split the intermediate tube sheet at the point where the temperature gradient is about 400F or less. The detailing could get a bit tricky but by leaving the top row of tube holes open ended, we could achieve this.

One could think of Incoalloy 800H or 50Cr-50Ni castings for the high temperature zones.

S.C.Sekhar
 
For 2098 Deg. F you could used HP40Nb (0.4C/25Cr/35Ni/Nb)
Alloy 800H and 50/50 are not suitable.
 